It become a little bit fun.... Byte 194 is Outdoor heat exchanger middle temperature .... But only when Byte 199 is greather then 0x03 ( so when extra query exist) , otherwise is a part of power generation... |
Beta Was this translation helpful? Give feedback.
-
And Byte 193 is Zone 2 pump speed [rpm] - Convert to DEC (X-1) X 50 |
Beta Was this translation helpful? Give feedback.
-
For DHW Circulation and Electrical Anode byte 199 must be equal or greater then 0x05 ,then service cloud start to interprete this byte 115 and 121 .... |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
-
In Servicecloud i can see new positions:
Also not sure ,if we have already this:
-SHP control [ 1:Disable 2:Enable]
-SHP flow control( forbid deltaT)[ 1:Disable 2:Enable]
Maybe somone have new HP with this features , and can pass a log ?
EDIT:
Byte 10:
7th & 8th bit = SHP Control b01 - Disable b10 - Enable
5th & 6th bit = SHP Flow control( forbid ΔT) b01- Disable b10 - Enable
Byte 115:
1st & 2nd bit = DHW Circulation b01 - off b10 - on
Byte 121:
1st & 2nd bit = Electrical Anode : b01 - off b10 - on b11 - Error
For DHW Circulation and Electrical Anode byte 199 equal or greater then 0x05 ....