Replies: 4 comments 8 replies
-
No, stop is to prevent overheating. |
Beta Was this translation helpful? Give feedback.
-
I don't get how it should be helpful: I might try to decrease the max. temp. of my DHW buffer a bit, but afraid to risk my marriage. |
Beta Was this translation helpful? Give feedback.
-
The compressor turns off because after switching from DHW to heating the target temperature drops so much that the difference between target and outlet is bigger than 2K. |
Beta Was this translation helpful? Give feedback.
-
I know simpler way to change from DHW to Heat without stopping ( but it have to be a twin-fan outher unit). When DHW is already heated to set temperature it waits 2(or)3 min and then changes to Heat. Just before that ,first you do Force Defrost , and after 30 s you switch to Heat. Some little defrost ( if any ) will perform , but it will be in Heat mode. As for single fan units each defrost couses at least one stop of compressor , it will not make this trick. |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
-
Hi, with my LT cascade installation I am heating up once per day the ~500l DHW buffer (operationMode 3 ; forceDHW 1).
I notice that each change on the Three-Way-Valve seems to trigger a compressor stop by the built in control SW of Panasonic. Probably they do so because of worries that during change of the Three-Way-Valve there might be some seconds of complete blockage. However, my Orkli 40713200 valve seems to be designed like "always non-blocking".
So I am thinking of
Goal 1: Avoid 2 compressor starts per day during heating time.
Goal 2: Optimize the target temperature during heating: Initially: Start with current DHW buffer temp + 1K, then increase to target temp +2/3 K. (Idea: Do never cool down the upper hot layer in the buffer).
Any thoughts / experiences? Or even confirmation of my observation "switch over always causes a compressor stop"?
P.S. Here a graph about a DHW cycle, started at 12:02:
From the logfile:
2025.01.07 12:25:13 1: Cooling down: wp2out=52.50 wp2target=55 wptarget=39 newtarget=51
2025.01.07 12:26:13 1: Cooling down: wp2out=46.25 wp2target=51 wptarget=39 newtarget=45
2025.01.07 12:27:13 1: Cooling down: wp2out=41 wp2target=45 wptarget=39 newtarget=40
2025.01.07 12:28:13 1: Cooling down: wp2out=40.50 wp2target=40 wptarget=39 newtarget=39
Beta Was this translation helpful? Give feedback.