How the boiler interprets parameter 730, 1030 for heating circuits? #401
-
Hi, So it is time to switch to winter mode as the temperature dropped to close to 0 outside during the night. I've had both 730 and 1030 set to 11 Celsius, but I cannot see that the boiler would really kick in when the temperature drops bellow 11 outside. Thanks in advance! Gábor Szabados |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 7 replies
-
Hi, Well, in general the parameters were right, as they define the value for the summer/winter mode. And yes, I think it's 8703 that counts. So it can happen in this period, that it's too warm during the day (before) and that the boiler doesn't kick in because of that. But if the temps drop down to 0°, this shouldn't occur of course.. Btw: whats the temp value you set in 714&1014? Cheers |
Beta Was this translation helpful? Give feedback.
Hi,
if I can help, I definitely will :)
Whats the type, model an controller you are using btw? Did you send us the output of /Q? Cuz I don't find you in my userlist..
Well, in general the parameters were right, as they define the value for the summer/winter mode. And yes, I think it's 8703 that counts. So it can happen in this period, that it's too warm during the day (before) and that the boiler doesn't kick in because of that. But if the temps drop down to 0°, this shouldn't occur of course..
So first, try to set this value (730&1030) HIGHER, e.g. to 16°. That means, that the boiler will switch from summer to winter if the 8703-temp drops below 16°. Right now it has to drop below 11° wi…